    Default D3400 Fuel Line

    Is it possible, can a D3400 run on a 1/4" fuel line or should it be a 3/8?" I had one made at a shop, and they made the wrong size. Just wondering if it can be used or if I need to get another one made.

    Thanks for the help,
    Jim Legge
    in Nova Scotia

  2. #2
    Join Date
    Nov 2006
    Location
    California City, CA USA
    Posts
    187

    Default Should work ok

    A 3400 engine probably burns only ~2 gal per hour under full load. That amount should flow fine through 1/4" tubing. Gravity purging/filter filling would take longer. The 3/8" line would would be less prone to vibration so the smaller line may need additional support (baling wire, nylon wire ties, etc.).

    Daron

  3. #3
    Join Date
    Dec 2006
    Location
    Nova Scotia
    Posts
    122

    Default

    That's great, Daron, thanks for the info.